Hi all... How can I connect Burkett batch controller electronics SE35 (manual attached) with pulse output to PLC? I think that I need to connect pulse output from controller to HSC? Every suggestion is welcome. Thank's AttachmentDS8035-Batch-EU-EN.pdf (802 Downloads) |
6/11/2014 8:43 PM | |
Joined: 8/16/2010 Last visit: 6/18/2025 Posts: 640 Rating:
|
Datasheet
AttachmentMA8025-8035Standard-EU-EN.pdf (848 Downloads) |
6/12/2014 7:19 AM | |
Joined: 8/16/2010 Last visit: 6/18/2025 Posts: 640 Rating:
|
Thank's. But I'm little bit confused. On Fig 21. on PLC side I have + and - 5-36VDC? I need to connect P+ output of the device to HSC input of PLC, and P- from 0V of my power supply. (see attached doc.) Specification: frequency is from 0.6 to 2200Hz, HSC is 100Hz. Is that essential for accuracy of flow? How to handle that on TIA side? Attachmentpulse.pdf (862 Downloads) |
6/12/2014 12:29 PM | |
Joined: 7/7/2010 Last visit: 9/5/2025 Posts: 16061 Rating:
|
HSC is up to 100kHz which is plenty of counting capability for your device. |
science guy |
|
6/12/2014 12:33 PM | |
Joined: 8/16/2010 Last visit: 6/18/2025 Posts: 640 Rating:
|
Oh yes...my fault. Thank's huggy. Is my wiring diagram from previous post ok? |
6/12/2014 12:46 PM | |
Joined: 7/7/2010 Last visit: 9/5/2025 Posts: 16061 Rating:
|
At a glance if looks like exactly how I would expect it to work. |
science guy |
|
6/12/2014 12:57 PM | |
Joined: 8/16/2010 Last visit: 6/18/2025 Posts: 640 Rating:
|
OK...Thanks a lot. |
8/20/2014 8:50 PM | |
Joined: 7/7/2010 Last visit: 9/5/2025 Posts: 16061 Rating:
|
Sounds right to me. |
science guy |
|
8/20/2014 9:56 PM | |
Joined: 8/16/2010 Last visit: 6/18/2025 Posts: 640 Rating:
|
Yes you are right. f=kxQ => Q=f/k => frequency (ID1000) [p/s] / 66,5 [p/l] So i get flow rate in litres per second? |