7/2/2013 10:31 AM | |
Joined: 7/8/2009 Last visit: 6/7/2025 Posts: 1977 Rating:
|
I think it should be with you in catalog |
Last edited by: Vithani at: 7/2/2013 10:34 AMcatalog link added I dont Like people driving Fast, thats the reason I overtake them ;) |
|
7/2/2013 10:42 AM | |
Posts: 262 Rating:
|
HI, Hope the below reply will help you:- for 3VU (@415Volt- AC Supply) The breaking capacity of 3VU13 is 100kA upto 6A. However for 3VU circuit breakers with rated current of 8A and 10A the short-circuit breaking capacity is 10kA. For circuit breakers with rated current from 16A to 25A the short-circuit breaking capacity is 6kA. In order to enhance the breaking capacity to 50kA, for these ratings (8A to 25A), the current limiter can be used. Thus the need of back up fuses is obviated. For 3RV @ 400V- AC 1) 3RV20: 20/ 55/ 100 (KA) ... upto 40A 2) 3RV21: 55/ 100 KA... upto 32A 3) 3RV23: 20/55/100 KA.... upto 40A 4) 3RV24: 55/100 KA....... upto 25A 5) 3RV10, 11, 13: 50/ 100KA...... upto100A 6) 3RV10 63& 3RV10 73: 120KA 7) 3RV1364 & 3RV1374: 200KA Please refer the attachment for complete details about 3RV AttachmentMPCB1.pdf (674 Downloads) |