Hi ! For example, I have some problems with the config in picture attached : impossible to have a 4-20mA signal on AQ card with a S7-300 whereas I have no problem from a S7-1500 with the same HW ET200 modules. Could you help me ? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/14/2023 12:27:13New subject after splitting |
|
11/14/2023 9:05 AM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
looks like you have not installed the needed HSP for the ET200SP IM. |
11/14/2023 9:16 AM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
as long you do not tell which problem you have exactly 🤷♂️ |
11/14/2023 9:34 AM | |
Posts: 9 Rating:
|
My colleague effectively used Step7 v5.6 (see printscreen) |
11/14/2023 10:00 AM | |
Joined: 5/12/2006 Last visit: 9/2/2025 Posts: 22709 Rating:
|
open properties of S7-300 PLC in HWConfig and check herer the process image size |
11/14/2023 10:19 AM | |
Joined: 3/11/2019 Last visit: 9/1/2025 Posts: 1653 Rating:
|
How do you program communication blocks FC11 and FC12 for the PROFINET IO controller? |
Feedback appreciated, please rate |
|
This contribution was helpful to
1 thankful Users |
11/14/2023 10:22 AM | |
Posts: 9 Rating:
|
Right ! I just have found the same ;-) |