2/21/2023 9:45 AM | |
Joined: 2/5/2020 Last visit: 1/13/2025 Posts: 8 Rating:
|
Hw config situation |
2/21/2023 10:05 AM | |
Joined: 7/9/2015 Last visit: 8/29/2025 Posts: 4443 Rating:
|
Hi, If you get 7FFF it means a broken wire. So check wiring / cable. Also check this FAQ: How can I tell whether a broken wire or a measured value overflow is responsible for the measured value "7FFF"?Regards, Towome |
|
|
3/8/2023 10:24 AM | |
Joined: 2/5/2020 Last visit: 1/13/2025 Posts: 8 Rating:
|
Thank you for your reply. I plan to check the wiring deeply but now it is not possible when production is in action. These two signals are not important so we can work with this error. Today is 8.03 on diagnostic buffor is no error, on module also. I upload behaviour of module, very strange is fact than changing max min value was also when plug from module was removed. This suggests that problem should be in memory access or etc.
Attachmentai8_13bit.avi (678 Downloads) |
3/8/2023 10:27 AM | |
Joined: 2/5/2020 Last visit: 1/13/2025 Posts: 8 Rating:
|
|
Follow us on