Hello. So, you have 850A armature/30A field drive and want to run 60A armature/2.8A field motor. Refer to chapter 6.6 of themanualabout load and shunt resistors for armature/field curcuits, which may be removed for reducing rated converter armature/field currents. Also don't forget to reduce this currents in parameters P072, P073, as described in chapter 7.5.
|
This contribution was helpful to
1 thankful Users |
1/17/2017 3:25 PM | |
Posts: 1 Rating:
|
Please chek cable conection ot terminal block,mcb,nfb. Maybe blow/heat Thnks Dani |
5/30/2017 5:59 AM | |
Joined: 8/25/2006 Last visit: 9/15/2025 Posts: 2218 Rating:
|
Hello. Look here. |
9/15/2017 9:00 PM | |
Posts: 3 Rating:
|
We face the same problem with the same drive and was solved by reducing set point in p102 |