4/25/2019 1:46 PM | |
Joined: 3/14/2008 Last visit: 9/11/2025 Posts: 2216 Rating:
|
Hi Microman, This problem occurs when the PCS7 hardware catalog does not contain the correct GSD file. Because of this, the system cannot determine the diagnostics and thus an error is generated. You must make sure the correct GSD file is imported in the hardware catalogus. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
1 thankful Users |
4/25/2019 2:36 PM | |
Joined: 3/14/2008 Last visit: 9/11/2025 Posts: 2216 Rating:
|
Hi, Yeah, only modules from PCS7 catalog are released...You need to check if the device is supported in the PCS7 Released Modules. PS: The link is for V9.0 SP1, but you may need another version. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
1 thankful Users |
4/25/2019 5:43 PM | |
Joined: 11/29/2011 Last visit: 2/4/2025 Posts: 1362 Rating:
|
Hi, OK! The PCS7 version is V7.1. I checked the SIMATIC Process Control System PCS 7 Released Modules (V7.1) list it is not in it. Is there a way to overcome this issue? |
- What you read here, please check with manuals and your requirements. |
|
4/25/2019 7:25 PM | |
Joined: 3/14/2008 Last visit: 9/11/2025 Posts: 2216 Rating:
|
Hi, I have to check in my files for a workaround (can check this evening/tomorrow), but if you remove the channel driver block for each input of the module and use a simple scale block from the standard library , then you won't have the issue...but then you lose the diagnostics capability... Since v8.1 the "Generate Module Driver" option is enabled by default, so if you remove the check during AS compile, you can compile without problems but next AS compile, the option is re-enabled automatically. |
If I could help you, you can use the RATE button. Thank you. |
|
4/26/2019 8:14 AM | |
Joined: 3/14/2008 Last visit: 9/11/2025 Posts: 2216 Rating:
|
Hi MicroMan, I inserted a ET200B module from the standard catalog and tried to compile and download. This works, no driver block connections are generated..Even it is not supported by PCS7, the compiler does not complain about that. So, I think the issue is that the slave is unknown in your hardware catalog... If you go to CFC chart and right click the input address and select: "Go to IO module", does that work? If not, the slave is not recognized.. |
If I could help you, you can use the RATE button. Thank you. |
|
4/26/2019 5:17 PM | |
Joined: 3/14/2008 Last visit: 9/11/2025 Posts: 2216 Rating:
|
Hi, What if you delete all the @charts in the project and run AS compile again? |
If I could help you, you can use the RATE button. Thank you. |
|
4/29/2019 12:23 PM | |
Joined: 11/29/2011 Last visit: 2/4/2025 Posts: 1362 Rating:
|
Hi, Only @CPU @ chart exist. If I delete that it does not make any difference. Anyways I noticed a warning in log. "(---) Not Supported" See the attachment. Attachment20190429_Module driver.txt (679 Downloads) |
- What you read here, please check with manuals and your requirements. |
|
4/29/2019 8:37 PM | |
Joined: 3/14/2008 Last visit: 9/11/2025 Posts: 2216 Rating:
|
Hi MicroMan, Can you give me some more info like: - MLFB number of the configured Simocode slave and it's modules - The used driver blocks in CFC chart (please attach a print screen also) - Are you using PCS7 V7.1 without service packs? And Simocode pro V7.0 Upd2 correct? - GSD file name of the Simocode slave I will investigate this further. It looks like some hardware configured is not supported by the system. |
If I could help you, you can use the RATE button. Thank you. |
|
4/30/2019 3:30 PM | |
Joined: 3/14/2008 Last visit: 9/11/2025 Posts: 2216 Rating:
|
Hi MicroMan, According to the manual, you are using the correct MLFB and GSD file. Are the defined inputs/outputs of the Simcode slave within the process image of the CPU? I saw your other post of the supporting CPU. Is this CPU released for PCS7 V7.1? That maybe a problem if it is not and could be related to your issue with Simocode. What if you create a copy of the multiproject and replace the CPU by a released CPU? Please select PCS7_V71 catalog instead of Standard catalog in hardware configuration to see the released modules. MicroMan: Did you do a proper update? I mean, did you mix different versions of driver blocks for example? If there are different versions, it may be that the system returns errors , please check if libraries are updated correctly and not mixed |
Last edited by: Oreca at: 04/30/2019 17:28:44If I could help you, you can use the RATE button. Thank you. |
|
2/10/2023 10:22 AM | |
Joined: 8/21/2020 Last visit: 11/3/2023 Posts: 1 Rating:
|
Thanks for your help. |