(0)| 3/24/2022 11:01 AM | |
|
Joined: 8/3/2009 Last visit: 1/16/2026 Posts: 16644 Rating:
|
Hello The User Administration whould work the same on HW as in Simulation (WinCC Basic/Comfort/Advanced). The only difference is in loading. If you start Simulation then the User Administration will always be imported automatically as in engineering project. On a real Panel or RT you have to activate the downloading/overwriting of the Useradministration while loading the project to the Runtime. only then the Users are available in Runtime. Check with a userview control in your simulation if the user is logged in properly and in the correct group. Check also your task using the Usergrout for dynamisation of the visibility of the screen items you want to show or hide if a special user/usergroup is logged in. (if something goes wrong you can also try to reset the temp data: https://support.industry.siemens.com/cs/de/en/view/109778709 ) Bye Murof |
|