if the plc s71200 the led of Run/Stop open with orange led and i cant go online what shouid i do ? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/18/2022 11:47:05New subject after splitting |
|
8/18/2022 1:28 PM | |
Posts: 71 Rating: (28) |
Hello Ali_Ismail, I recommend you to check the online & diagnostic section of TIA Portal and see if there is any error. You can take a look at the meaning of the LEDs status in s7-1200 manual: Status LEDs https://support.industry.siemens.com/cs/ww/en/view/109797241/143378556043 Best regards, s7-mencey. |
Last edited by: s7-mencey at: 08/18/2022 13:28:19 |
|
8/30/2022 11:06 AM | |
Joined: 3/11/2019 Last visit: 10/8/2024 Posts: 1586 Rating: (289) |
Dear Ali_Ismail, the error LED of an S7-1200 is always red. So if you see a "light orange", i assume the led is "off" but you can see the yellow/orange light from the Run LED. So asume the LED state is: Run -> yellow Error -> off Maint -> blinking yellow According to the manual-> "Remove the memory card" Are you using the cpu with a simatic memory card and is the card configured as transfer card? regards sancruz
|