Hi there! What you have here is a TO alarm 103, see here: https://support.industry.siemens.com/cs/ww/en/view/109781853/136082365067 For one, the complete error message should provide closer information about the detailed cause, so try getting the complete message. Also as you can see this is a configuration error (number range within 100), and as the manual states it can only be acknowledged by doing a TO restart. To do this, call MC_Reset, set its input Restart to TRUE, then execute it. Regards, |