Hello, if you need to integrate RDG thermostats via PXC001.E-D, then I will suppose to use them as S-Mode device and you will need to do engineering via ETS. >Then you have to export the project and import it to the PX KNX Tool. >In the PX KNX Tool then can be created all datapoints from KNX to the BACnet. See attached document. AttachmentCM1Y9777en_05.pdf (738 Downloads) |
Best regards, |
|
3/10/2023 9:33 AM | |
Joined: 6/13/2016 Last visit: 6/13/2024 Posts: 13 Rating: (2) |
Cant download it, and cant find it even when I am logged in. BR |
3/10/2023 11:25 AM | |
Joined: 7/25/2012 Last visit: 11/7/2024 Posts: 278 Rating: (84) |
Here you have it: AttachmentCM110748en_13.pdf (387 Downloads) |