If an OB cycle which you use for counting is longer than pulse duration then you won't be able to count correctly because of the reason you gave. With this CPU you have two options:
This manual may be of help. |
Last edited by: jacek d at: 07/11/2023 10:12:11Regards, |
|
This contribution was helpful to
1 thankful Users |
7/11/2023 10:09 AM | |
Joined: 3/30/2020 Last visit: 9/2/2025 Posts: 5416 Rating:
|
Using continuous high speed counting would be best. Have a look at the materials offered here: [Search: "31xC counting"]. These articles are centred around Step7 Classic but still applies for Step7 (TIA Portal). Important: Do not work with REAL numbers. Work throughout with DINT when adding counting numbers to each other. Only the step where values are displayed to the user do you use REAL numbers to show the engineering unit. These articles may also be of value: [Search: "totalizer"] |
Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
This contribution was helpful to
1 thankful Users |
7/11/2023 11:56 AM | |
Joined: 3/12/2019 Last visit: 8/1/2023 Posts: 4 Rating:
|
Thanks, I read through the manual but still unclear to me. do you have example of the the first option? or maybe reference to a document. option 2, we don't want to add extra hardware. |
7/11/2023 12:04 PM | |
Joined: 3/12/2019 Last visit: 8/1/2023 Posts: 4 Rating:
|
Thanks, HSC can also be used for flowmenter? because I assume the flowmeter noramlly is not high speed. |
7/11/2023 12:24 PM | |
Joined: 9/23/2005 Last visit: 9/2/2025 Posts: 5112 Rating:
|
Learning to use the Knowledge Base can be a competitive advantage. |