Dear forum member, You should be able to find this information in the PXC001 MODBus documentation 016_PX_Modbus_CA2Y9772en_06.pdf (link: https://sid.siemens.com/v/u/A6V10689927 ). See page 22/23, chapter 4.1.2 Mapping information two Float Swap conversion 1 and 9. You can set in MappingInfo6 (-> as described below) -> first I would check with one point with the conversion parameter 1 (-> Swap Rgisters, where the 16bit registers will be swapped) if this should not work then I would also try with the conversion parameter 9 (-> SwapBytes, where first the register are swapped and then in the registers the two bytes too), as shown in the attached print screens below. Best regards, Albis