Additionally, I am attatching connection in HMI section. |
| 8/18/2023 7:22 AM | |
|
Joined: 2/17/2020 Last visit: 1/16/2026 Posts: 1251 Rating:
|
Hello, Few points to keep in mind in this case: - If both PLC and HMI are simulated, does the communication between them work? - Is it a direct connection or does it go through some intermediate element, such as a router? Have you tried other PN/DP cables? - Do the date and time configured in the PLC and HMI match? Please see: No connection to PLC after WinCC Panel Images V17 Update 6 - In the PLC tag table, do the tags that are shared with the HMI have the "Accessible from HMI/OPC" and "Writable from HMI/OPC" checks marked? I hope this helps to find the source of the problem! |
|
A rating will be well appreciated. |
|
| 12/14/2023 2:37 PM | |
|
Posts: 1 Rating:
|
did you find the solution? |