Hello! Tell me you can make the replacement of the control module CU240S DP to CU250S 2DP with the loading of parameters from cu240 to PE g120 siemens? terminal blocks on which the wires are wired are the same. Thank. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/17/2019 09:52:02New subject after splitting |
|
6/17/2019 9:11 AM | |
Joined: 10/11/2006 Last visit: 10/18/2024 Posts: 5925 Rating: (810)
|
Hello Lexx-79, a direct parameter migration from CU240S to CU250S-2 is not possible due to the different parameter structure of the new SINAMICS generation.You have to recommission the drive. You can find additional information and tips regarding migration on the following SIOS FAQ https://support.industry.siemens.com/cs/ww/en/view/70021820 |
With best regards, |
|
4/25/2024 8:11 PM | |
Joined: 10/2/2021 Last visit: 9/24/2024 Posts: 6 Rating: (0) |
Hello, This migration tool worked for me: [snip] Regards, gnazareth. AttachmentSinamicsMigrationTool-20240426T082726Z-001.zip (255 Downloads) |