(4)| 1/21/2025 10:26 AM | |
|
Joined: 5/30/2022 Last visit: 1/20/2026 Posts: 634 Rating:
|
Hi Luh_Days, 1- Have you assigned the periphery to a PLC? 2- Please install the HSP for V19 and configure the ET200SP by catalog instead of GSD and try to solve your problem: 3- Check that you are following the correct procedure: Assigning a PROFIsafe address of the F-I/Os with SIMATIC Safety |
|
If this information really helps, you could use the Rate function. |
|
This contribution was helpful to
|
|
| 1/21/2025 10:29 AM | |
|
Joined: 7/9/2015 Last visit: 1/23/2026 Posts: 4501 Rating:
|
Hi, you projected ET200SP with GSD - for this you need FCT for F-Adress assignment. SIMATIC S7-Fail-safe Configuration Tool (S7-FCT)Regards, Towome |
|
|
|
This contribution was helpful to
|
|