(0)| 9/6/2009 2:28 PM | |
Joined: 5/28/2008 Last visit: 1/22/2026 Posts: 4522 Rating:
Dear Tomy Master, Please chck that you had make parameters as follows: P0700 = 2 "Command Source = Terminals" P1000 = 2 "Selection of frequency setpoint = Analog Input" P1080= 0 " Min. Frequency" P1082= 50 "Max. Frequency" P2000 = 50 "Referenc frequency" This value is very important. It's the value which will be equivalent to 10V if your drive setpoint is analog and will equivalent to 4000Hex. if your command setpoint is profibus. Also check that you have connected the analog signal to pins 3 & 4 of your drive. Best regards, |