(3)| 9/10/2008 8:34 AM | |
|
Posts: 2930 Rating:
|
Hi, here adiitional notes to marcsinclairs post: 1. Unused analog inputs must be short-circuit. 2. Use shilded wires for your analoge sensor, grounding only at one side 3. Check if your analoge wiring is in parallel to high voltage/current wires. If so, change it Do you have ASi-Master, or SIWAREX modul connected to S7-200? If so, then use the right analoge chanel because this two modules use analoge I/Q to communicate to the PLC. Here an older but still actual FAQ from Siemens: http://support.automation.siemens.com/WW/view/en/2415890 I hope this helps. Helmut |
| 9/10/2008 9:39 AM | |
|
Joined: 9/7/2007 Last visit: 4/3/2025 Posts: 550 Rating:
|
Hi Gordon, I faced this problem once ago and I connected the shield the M and the result was good |
|
Best Regards |
|
| 1/25/2010 11:14 AM | |
|
Posts: 2 Rating:
|
I faced this problem too, hope this way can solve mine. |