May anyone tell me what I need to change to enable placing of two IM 153-2 redundancy moduls (6ES7 153-2BA00-0XB0) in same rack in HW config? Thanks in advance. |
| 1/26/2011 1:53 PM | |
|
Posts: 86 Rating:
|
Hi, Have you used a Simatic H system?? In simatic manager > insert new object > Simatic H system Yer |
| 1/26/2011 5:53 PM | |
|
Posts: 2 Rating:
|
Yes, I have used SIMATIC H system with CPU 414-H. |
| 1/27/2011 7:35 AM | |
|
Joined: 3/21/2006 Last visit: 1/10/2026 Posts: 10247 Rating:
|
Hello, I think question concerning 6ES7153-2AR03-0XA0 ET200M, IM153-2 INTERFACE REDUND.BUNDLE. Look at attachment. Is it enough, is it true? Best regards, Hristo Mihalev |
This contribution was helpful to
|
|
| 2/15/2011 8:34 AM | |
|
Posts: 37 Rating:
|
As aret says, you don't physically drag two IM to the rack, just one and make it redundant. |
Last edited by: gfair at: 2/15/2011 8:35 AM |
|