1/22/2012 4:18 PM | |
Joined: 4/30/2011 Last visit: 1/9/2022 Posts: 223 Rating: (4) |
How I can connect s7-1200 (CPU 1214) to DO Modul (SM 1222) at 30 m from each other ? Tks
|
1/22/2012 6:03 PM | |
Posts: 89 Rating: (16) |
By adding another CPU to your SM1222 DO module and connect both CPU's by Profinet. |
1/22/2012 10:11 PM | |
Joined: 4/30/2011 Last visit: 1/9/2022 Posts: 223 Rating: (4) |
ha) I know that!! need other way!
|
1/23/2012 4:31 AM | |
Joined: 8/31/2010 Last visit: 11/6/2024 Posts: 1523 Rating: (229) |
You can connect between a Max. distanceof 2m, for which this cable has to be used. - SIMATIC S7-1200, EXPANSION CABLE 2.0M- 6ES7290-6AA30-0XA0 If you need to connect signal modules to 30m distance, then it's ideal to go for a Decentralized periphery - either PROFINET / PROFIBUS DP / AS-i. (in that case SM 1222 can't be used - a suitable ET200 IM + Digital Output module must be used) |
Like it? Rate it! |
|
1/23/2012 8:35 AM | |
Joined: 4/30/2011 Last visit: 1/9/2022 Posts: 223 Rating: (4) |
Tks a lot, Bro I see
|
Follow us on