(0)| 3/22/2012 9:15 AM | |
Posts: 8092 Rating:
Hello Experts, In 6RA70 can the user set speed propotionate current limits? If so by which parameters. Thanks in advance. DEEP. |
| 3/22/2012 9:19 AM | |
Joined: 8/25/2006 Last visit: 1/21/2026 Posts: 2221 Rating:
Hello. You need not any additional things for this. Just look at function diagram sheets G160, G161 of 6RA70manualand select required torque (and current) limits in parameters P171, P172, P605, P606, P603, P604. Also look at parameters P169, P170 (selection of torque/current control). |
| 3/22/2012 9:53 AM | |
Posts: 8092 Rating:
Hello KSN, Thank you very much for your reply. As suggested by you, I have gone thru the diagrams. I have following queries. 1. Agreed I can set current limits in both the directions. But I want 250% ofboosting torque by the rated torque only for starting, how to set it? The time base for this torque is it adjustable? 2. Speed depedent current limit as showed in sheet G161 is at two different speed is OK. What I would like to know is, can user set such current limits during starting? My queries sounds littlebit crazy!!! Ok. But please help. DEEP. |
| 3/22/2012 10:35 AM | |
Posts: 8092 Rating:
Hello. Thanks for your reply/suggestions. I shall check the same & in case if requires some help, shall revert back. Thanks, DEEP. |