4/19/2012 2:59 PM | |
Posts: 153 Rating: (2) |
I have attached screen shot of diagnostic buffer and event id id 16#F1C8:0836Attachmentuntitled.zip (193 Downloads) |
4/19/2012 3:08 PM | |
Posts: 3093 Rating: (323)
|
Hello Anit, obviously it is a bug of the simulation software. It sends either a wrong CRC or a wrong length information. Regards, Kaulquappe |
4/20/2012 7:33 AM | |
Posts: 153 Rating: (2) |
hello smiffy, I have attached screen shots of instant DB with and with out polling from mod scan32. My slave id is 222, parity = even, stopbit=1 and cable connection of cp and cpu as: cp cpu 2 = 3 3 = 2 5 = 5 please solve my problem where I am wrong???? Attachmentinstant_db.zip (180 Downloads) |
4/21/2012 5:47 AM | |
Posts: 153 Rating: (2) |
hello smiffy, Kaulquappe Now my system is running good as well as with modscan and also with another modbus master system. I were making correct parameter setting as you guys discussed. I found some fault in my serial cable , I removed old connectors and placed new connectors only. Anyways thanks a lot.......keep it up
|
This contribution was helpful to3 thankful Users |