10/28/2013 9:31 PM | |
Posts: 62 Rating: (0) |
:( I can not create a Tag with a custom PLC data type ? The data types are no choose able. |
10/28/2013 10:40 PM | |
Posts: 62 Rating: (0) |
Can you put a screen shot ? Thanks I do not know what I'm doing wrong :( |
10/29/2013 7:41 PM | |
Posts: 62 Rating: (0) |
Hello, I can not get this to work .... What I'm doing wrong ? see picture |
Last edited by: _Kalle_ at: 10/29/2013 7:54 PM |
|
10/30/2013 6:35 AM | |
Posts: 5 Rating: (1) |
Hi., Go online then you press monitor all button in Data block..... also i attached the file for reference |
10/31/2013 3:13 PM | |
Posts: 62 Rating: (0) |
huggy_d1, what I'm doing wrong ? Could you paste a screenshot ? |
10/31/2013 4:00 PM | |
Joined: 7/7/2010 Last visit: 10/11/2024 Posts: 15292 Rating: (2427)
|
Ok, I have confirmed that you technically can do the things I said, but unfortunately, not the way I had thought that they worked. From the DB view with monitoring active, you can take a snapshot, edit the start value, and update the plc from the new start value. Probably not a good idea for some things, but may be ok for recipe type data. From the datatype copy/paste issue, I confirmed it will not copy/paste properly just as you have experienced. I found that if the custom datatype was of a certain type, it would copy/paste very well, just not so well for the watch table. At this point, it would be good to submit a Support Request and see if they can find a work-around and hopefully get a fix added to a future update to V12. |
science guy |
|