3/13/2014 2:53 PM | |
Posts: 67 Rating: (1) |
I work with redundancy system. I want to know what is 'pending' and 'hidden' alarm in Alarm Control (at bottom right). I'm understand 'to acknowledment'. Thanks. |
3/14/2014 10:04 AM | |
Joined: 12/12/2011 Last visit: 12/30/2020 Posts: 821 Rating: (40)
|
Hi, Hidden = It is possible to hide alarms, that they don`t disturbe the operator, e.g. if you upgrade a part of the plant, you could hide all the alarms of these part. Pending = The reason of the alarm is still persist and not gone. Best Regards, Healthcheck |
Grundkurs/Systemkurs WinCC V7: |
|
3/18/2014 2:49 PM | |
Posts: 67 Rating: (1) |
Let's see the picture [snip] ... You see, I just have 104 list. What I do not understand is pending (430). How to show the pending alarm? AttachmentD:\tmp\upload\alarmpending.zip (124 Downloads) |
Last edited by: CS Moderator at: 3/19/2014 9:00 AMPicture attached Last edited by: ucon89 at: 3/18/2014 2:50 PM |
|