Hello, Sampling time of FB1(CONT_C) in CFC is automatically adapted from the OB3X calling rate. You can check the online values of the assigned DB to the loop to find out the reason .If you want to provide clues to help, we need online snapshots(videos) of all shwon variables at the same time .Also, share your logic regarding the PID controller (OB3X,OB100).