7/28/2014 11:01 AM | |
Posts: 55 Rating: (0) |
I know there are other thread there about this problem but I have go through everything and still can not get the WinCC talk to PLC Settings: _ CPU315-2DP with CP343-1 _ PC Dell Poweredge T110 running win7, freshly install with Step 7 v5.5, WinCC v7.0 sp3 and Simatic Net v12 Problem: I can connect and online with S7 program, but can not get the WinCC to work Have been try alot of different things such as: _Change the parameter between "S7Online" and the setting in the PG/PC inteface _Install simatic Net v12 _Change Slot number in "connection parameter" between 2 (CPU315-2DP slot) and 7 (CP343-1 slot) _I also try to connect from PC to another PLC i.e: IM151-8 PN and the WinCC works perfectly I have no idea what is the problem. Can some experts please help me on this? Attached are some pics Thank you so much Hoang Tran Attachmentwincc problem.zip (87 Downloads) |
7/29/2014 9:43 AM | |
Posts: 457 Rating: (46) |
Hello, I think problem will be solved by using a MPI connection. CPU 315-2DP has only MPI connection. Please find here: http://support.automation.siemens.com/WW/view/en/31510992 a complete FAQ for setup. In WinCC (Tag management) use MPI connection (see WinCC help). Hope this helps. Georg |