Hi,
What can i do?
---------------------------------------------------------------------------------------------------- |
Last edited by: Min_Moderator at: 7/31/2015 11:20:02 AMNew subject after splitting |
|
7/31/2015 12:33 PM | |
Posts: 739 Rating: (55)
|
F011. Internal Interface fault. This occurs when there is a communications failure between the power section ( Bottom Board) and the control section ( Top board). It is usually necessary to remove power then switch on again. This fault can be caused by EMC problems such as transients on the supply, poor earthing etc.; or by a defect, inside the drive (Power section, electronic board, cable). Your MICROMASTER (6SE30…) is quite old and there are now more spare parts available.
I suggest to trash it. 6SE3013-4BA00 MM75 / Technical date 0,75kW 1AC 230V +/-15% / 2AC208V+/-10% IP20/ IP21 without filter
As new type I suggest using a SINAMICS G110 6SL3211-0AB17-5UA1 Technical date: G110 CPM110 1AC230 0,75KW UF AIN IP20 (See: https://support.industry.siemens.com/cs/ww/en/pv/6SL3211-0AB17-5UA1/pi)
|
This contribution was helpful to1 thankful Users |
7/31/2015 5:40 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello HartungGER, Have a look at page 8 for the fourth digital input "DIN 3": Operating Instructions (Compact) Issue 11/04 SINAMICS G11 |