10/23/2015 7:26 AM | |
Posts: 1 Rating:
|
Hi , HOW TO MAKE PROGRAMME FOR ANALOG INPUT 4-20mA USING RTDT AND GETTING OUTPUT CAN ANY ONE PLEASE ASSIST. WHICH PROGRAMME BLOCK CAN BE USED IN TIA- S7-1200 ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 10/23/2015 11:27:44 AMNew subject after splitting |
|
10/23/2015 3:42 PM | |
Joined: 7/7/2010 Last visit: 9/10/2025 Posts: 16079 Rating:
|
What is RTDT? Analog input signals range from 0-27648 for 0..20mA or 4..20mA if your module allows you to choose. Just use the scale block to adjust the 0-27648 to your user units for whatever an RTDT is and use the resulting scaled value.
|
science guy |
|
10/23/2015 4:49 PM | |
Posts: 8946 Rating:
|
If you are talking about RTD, you can not use a 4..20mA Input. |
10/23/2015 4:56 PM | |
Joined: 3/28/2015 Last visit: 8/15/2025 Posts: 725 Rating:
|
Hello, I think RTD connected to temperature transmitter and take the O/P from it(4-20 mA) |
Eng.Mohamed Ibrahim |
|
10/23/2015 7:30 PM | |
Posts: 8946 Rating:
|
Also, this link may be helpful: |