Posts: 163 Rating: (2) |
Hello, Yes, this is the AI module. |
2/14/2016 5:39 PM | |
Joined: 9/27/2006 Last visit: 11/18/2024 Posts: 12294 Rating: (2691) |
Hello ldir; The message you show is titled "Area length error when reading" for address 288, and mentions that OB 121 is not loaded on your CPU. OB 121 is called by the OS of the CPU when there is a programming error, or when you try to access an address that is not available. Start by creating an empty OB 121 and downloading it to the CPU. This operation is explained in detail in the following FAQ:
Which organization blocks can you use in STEP 7 (TIA Portal)?
https://support.industry.siemens.com/cs/ww/en/view/40654862 Loading the appropriate error OB allows the CPU to collect more information on the fault and load it in the diagnostic buffer. So next time the error occurs your diagnostic buffer should contain more precise messages on the fault. Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
2/18/2016 7:32 AM | |
Posts: 163 Rating: (2) |
Hi, this is what I get. even with Simatic Manager. :( Question: how to address an analog input? |