(0)| 2/17/2016 10:36 PM | |
Joined: 9/27/2006 Last visit: 1/14/2026 Posts: 12481 Rating:
Hello sandrao; Have a look at the technical data of your CPU (see attachment). Hope this helps, Daniel Chartier |
| 3/2/2016 11:42 PM | |
Hello Sandra; Have a look at chapter 6 of this manual:
SIMATIC ET 200SP Distributed I/O system
https://support.industry.siemens.com/cs/ww/en/view/58649293 This section will show you how to backup and restore the PLC configuration, how to upload from the device and how to upload the complete device as a new station. The table below shows that only the Backup from Online Device function is able to upload from a F-CPU such as yours. The procedure for Backup from Online Device is explained in section 6.2.4.2 of the proposed manual. Hoep this helps, Daniel Chartier |
This contribution was helpful to
| 3/4/2016 6:27 AM | |
Joined: 5/12/2006 Last visit: 1/14/2026 Posts: 22800 Rating:
Hello, upload of F_Blocks are not possible. Uploading the safety program to a programming device or PC (S7-1200, S7-1500) The "Load from device" function has not been released for S7-1200/1500 F-CPUs. This also applies to F-I/O in standard mode. SIMATIC Industrial Software SIMATIC Safety - Configuring and ProgrammingPage 272 https://support.industry.siemens.com/cs/de/en/view/54110126
Christoph |
Follow us on