Hi, I think it is not possible Read this recent Topic about the same question :
|
Last edited by: The Helping Hand at: 4/12/2016 9:40:21 AMMade the link clickable |
|
| 4/12/2016 12:43 PM | |
|
Joined: 8/3/2009 Last visit: 1/16/2026 Posts: 16644 Rating:
|
Hello LB_90 Its not possible in WInCC Advanced/Comfort/Basic. Only in WinCC Professional you can use a much better alarm Control and here you can use filter functions and other alarm Settings. Bye Murof |
Last edited by: Murof at: 4/12/2016 12:43:33 PMIf this Information really helps, you could use the Rate function |
|
| 4/12/2016 1:44 PM | |
|
Joined: 1/4/2013 Last visit: 1/13/2026 Posts: 1195 Rating:
|
LB, I had a similar problem one year ago where customer wanted to memorize some alarms and not some others , depending on their importance. At the end I made a simple "memorization" of the alarm log in my PLC instead of trying to hijack the standard alarm view... So I used an array where I have stored the alarm code and I visualized it in HMI. Trust me , it's smarter in these strange situations |
|