Hello marotaro, the yellow triangle with the exclamation mark means that the HMI has lost the connection to the PLC. Please check your PG/PC Interface in Windows (Start > Control Panel (View by: Small Icons) > Set PG/PC Interface. Make sure "S7ONLINE (STEP 7) --> " is connected to the correct network card, not "PLCSIM" or another false Network. Can you ping the PLC from the Operator Station? What WinCC RT is it? WinCC RT Professional? Which Version/Service pack/Update? Here is the link to an FAQ about WinCC RT Professional and the IDB, but I don't think it can help much in your case. But maybe?
|
|
~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ★ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ ~ |
|
This contribution was helpful to
|
|
| 5/27/2016 5:48 PM | |
|
Posts: 7 Rating:
|
see also in this attachement the connection config in WINCC. |
| 5/27/2016 7:33 PM | |
|
Posts: 7 Rating:
|
I solved the problem by using a backup that i had saved yesterday. |