Hi... I know that I can use this resistors... this article is one of more http://forum.allaboutcircuits.com/showthread.php?t=75714 So, for NPN sensor I need to use pull-up resistor. It must be connected between supply, and signal, and signal to PLC input...(image attached) PLC input - 2,4mA at 15VDC, supply 24VDC. R=24VDC/0,0024= 10kOhm is that good calculation??? |