8/30/2018 8:43 PM | |
Joined: 7/7/2010 Last visit: 11/15/2024 Posts: 15402 Rating: (2443)
|
Have you looked at the module manual? I found it here: https://support.industry.siemens.com/cs/ww/en/view/83727715 Is there a firmware revision difference between what is in your project and what is installed in the remote I/O system? Since there is a way to send the configuration parameters TO that module using WRREC (according to the module manual), you could in theory use RDREC to retrieve the configuration values and then use the manual to figure out the module's configuration manually. Do you have either German or English set up as a programming or project language in your project? If not, try adding English as a second project language. It is strange the things that get fixed by adding one of those 2 languages.
|
Last edited by: Jen_Moderator at: 8/31/2018 7:47:56 AMOptimized link. science guy |
|
This contribution was helpful to1 thankful Users |
9/11/2018 10:03 PM | |
Joined: 8/18/2014 Last visit: 11/5/2024 Posts: 59 Rating: (0) |
I installed the HSP but I still have the problem =S.
|