May I ask you? Is there any way to make the clock pulses faster then 10
kH? I have to write a data log file every 1ms interval. Thanks a lot in
advanced ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 4/1/2019 7:40:39 AMNew subject after splitting |
|
This contribution was helpful to1 thankful Users |
4/1/2019 9:03 AM | |
Joined: 10/16/2007 Last visit: 9/11/2024 Posts: 629 Rating: (45) |
With a S7-2100? |
This contribution was helpful to1 thankful Users |
4/1/2019 1:43 PM | |
Joined: 12/14/2017 Last visit: 8/12/2024 Posts: 3 Rating: (0) |
By using two timer you can make clock pulse of 1ms. |
4/1/2019 1:52 PM | |
Joined: 7/7/2010 Last visit: 9/26/2024 Posts: 15238 Rating: (2418)
|
You will not succeed in this. Logging at 1ms is best done by sending data to an external PC via UDP, and even then the s7-1200 will have difficulty.
|
science guy |
|
4/1/2019 2:00 PM | |
Posts: 2826 Rating: (685) |
Hello huggy_d1.
Have you ever seen a 10kH (kilo-henry) coil before!
How about a batch process? Record some cycles of values in a DB and then write the DB to the memory card. Do you think that would work? BR |
4/1/2019 3:25 PM | |
Joined: 7/7/2010 Last visit: 9/26/2024 Posts: 15238 Rating: (2418)
|
The option to collection an entire second of data and write to a memory card 1000 records makes much more sense than writing 1 record every 1ms. In the case of 10,000 writes per second, well, the s7-1200 is not able to perform that task without aggregating data - whether to an external PC or to a memory card. Maybe a data logging HMI with memory card would work better by aggregating data and having the HMI log it - assuming the s7-1200 PLC is for whatever reason a given. To log at 10,000 Hz on a s7-1200, you need the following: [more cyclic interrupts than you can create] ---If you could create them:
|
science guy |
|
4/5/2019 8:07 AM | |
Posts: 4 Rating: (0) |
It seems to me the only one way to log it sending data via UDP. Timers, cyclic interrupts have NO results. Many thanks! |