3/11/2020 11:45 AM | |
Posts: 5 Rating: (0) |
Hello, I have DMG CNC milling machine with Siemens 810D sinumerik control, i need to cancell the linear scale of the Y axis, and let the machine works with the motor encoder only,can any one help? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/11/2020 14:04:40New subject after splitting |
|
3/11/2020 2:46 PM | |
Posts: 5 Rating: (0) |
Thank you for your support. Would you send me the complete procedures to check the plc? |
3/12/2020 11:53 AM | |
Joined: 10/17/2007 Last visit: 10/11/2024 Posts: 4044 Rating: (354)
|
Pay attention, I have worked in a company with more than 30 DMG machine with 840D and 810D. I suggest you check DMG manual or contact them. as I remember. there is an easy way to do what you want. you don't need to change PLC program--which is risky for you. DMG designed PLC program option. you only need to set some DBxx.DBXyy.z then follow their instruction
|
If you like my comments please |
|
3/12/2020 7:08 PM | |
Joined: 11/26/2016 Last visit: 10/8/2023 Posts: 138 Rating: (3) |
Hi; I attach a file that will help you. Note, you have to change the axis from c to whatever axis you want. AttachmentCancellig encoder.pdf (245 Downloads) |
Nothing IS IMPOSSIBLE. |
|
3/15/2020 7:32 AM | |
Posts: 5 Rating: (0) |
Thank you for your support, After setting the parameters you sent, can i make reference to the Y axis? Regards, |