Hi, Think of it in reverse, you need to Read, rather than Write. As an example, in AS02 you would add an AI to Read from an AI that exists in AS01. The AI in AS02 would be addressed with the B= prefix. If the TD for the AI in AS01 is Plt01'Inputs'CHWFT, then you bind the AI in AS02 to B=Plt01'Inputs'CHWFT. (Ensure the slope value gets set to 1). There is a look-up table that makes this easier to achieve. In AS02, go to Edit IO Addresses. Set the Subsystem for the AI to 'B', then right-click the Signal Address field, and select BACnet object selection. You can then browse into AS01, and select the associated point that you want to Read. See attached for reference. Give it a try, and come back if you're still not sure. Regards, AttachmentCaptures.zip (285 Downloads) |