10/9/2020 1:14 PM | |
Joined: 12/18/2014 Last visit: 5/28/2024 Posts: 33116 Rating: (4088)
Import of a technical question via PM from the user6boki6. Hi, I am learning about Logo but I have some problem that can't solve. I see that you are expert regarding Logo so can you make example maybe. I want control heating in house. Inputs are PT100 for measuring actual temperature in room (-50°-200°C) and user set temperature (via hmi like marker, or just via analog input as experiment). It need to give analog output 0-10V for heater. Can you make example ? Thanks. |
10/9/2020 2:05 PM | |
Take look at attachment. The setpoint can change over the LOGO! display. Also switching auto or manual for the PI controller over the display. AttachmentBoiler_temperature_control_0BA8.Standard.zip (323 Downloads) |
10/14/2020 7:33 AM | |
Joined: 10/26/2018 Last visit: 4/30/2024 Posts: 2 Rating: (0) |
Thank you! |
This contribution was helpful to1 thankful Users |