Hello Ssalda; Do you mean you want to control a stepper motor with an Automation Direct STP-DRV-6575? You will find the manual for this stepper controller in this webpage, each chapter is a different pdf download: https://cdn.automationdirect.com/static/manuals/surestepmanual/surestepmanual.html Look at the screenshot below, it states that the control signals for this drive should be a source of step pulses. This is reffered to as PTO (Pulse Train Output) and can be achieved in the S7-1500 with a special Technological module TM-PTO4. There appears to be no Profinet or Profibus interface (for ProfiSafe telegrams) or analog control options for this drive. SIMATIC S7-1500/ET 200MP Technology Module TM PTO 4 (6ES7553-1AA00-0AB0) Section: Pulse Train Output (PTO): https://support.industry.siemens.com/cs/ww/en/view/109742067/93614513035 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 12/02/2020 01:19:33Last edited by: dchartier at: 12/02/2020 01:43:43 |
|
This contribution was helpful to1 thankful Users |
12/4/2020 5:11 PM | |
Posts: 5 Rating: (0) |
Thank's a lot for the information! Very much appreciated Best Regards. |