5/18/2012 9:58 AM | |
Joined: 4/19/2008 Last visit: 2/9/2024 Posts: 1525 Rating: (159) |
Hello Rajkiran, Download the Catalog ST 70 2011from the Link you will find the all the Modue Detail here, & S7-1200 having on Board profinet port so, no need to used some special Cable Like PC Adapter... |
Ammy |
|
5/18/2012 11:44 AM | |
Joined: 8/31/2010 Last visit: 4/29/2024 Posts: 1509 Rating: (222) |
Hello RAJKIRAN, In addition to the ST 70 catalog you can use the SIMATIC Selection Tool to choose the required configuration. Enclosed is a typical configuration for your requirement. AttachmentS7-1200 Config.pdf (279 Downloads) |
Like it? Rate it! |
|
This contribution was helpful to2 thankful Users |
5/18/2012 1:53 PM | |
Joined: 8/18/2009 Last visit: 5/9/2024 Posts: 543 Rating: (33) |
Thanks Ganes10, but In PLC AI0 - 10V DC & IO module4 AI / 2 AO - +/-10V but I required 4-20 ma .....
|
Rajkiran Patil |
|
5/18/2012 2:13 PM | |
Joined: 8/31/2010 Last visit: 4/29/2024 Posts: 1509 Rating: (222) |
Hello RAJKIRAN, Don't use the onboard AI of the CPU, use only the SM 1234 for AI. SM1234can be configured as 0 - 20 mA (unfortunately no 4 - 20 mA) configurable in a group of 2 and also the resolution is 14 bits. If the requirement is more than that then we have to look for ET200M Signal modules. I missed to mention this in my previous post. |
Last edited by: Ganes10 at: 5/21/2012 9:42 AMmentioned as SM 1234 Like it? Rate it! |
|
5/21/2012 9:23 AM | |
Joined: 8/18/2009 Last visit: 5/9/2024 Posts: 543 Rating: (33) |
DearGanes10, now our I/O are revised so I dont want AO Signal in this configuration... then could I take 6ES7231-5ND30-0XB0(ANALOG INPUT SM 1231, 4AI 16BIT) instead of 6ES7234-4HE30-0XB0. |
Rajkiran Patil |
|
5/21/2012 11:00 AM | |
Joined: 8/31/2010 Last visit: 4/29/2024 Posts: 1509 Rating: (222) |
Hello RAJKIRAN, For 6ES7 231-5ND30-0XB0, you can use it as Voltage or current (differential) inputs. In this module you have both 0 to 20 mA and 4 to 20 mA configurable current input type. So you get a better accuracy compared to the previous module. The resolution is 16 bits. Also it can be configured as a individual channel (voltage or current) for all 4 channels, unlike the previous module. HSP 0026 is required to configure and use the same module in TIA Portal. STEP 7 v11 SP2 with Update 3 is also a prerequisite for this. |
Like it? Rate it! |
|