6/30/2020 2:22 PM | |
Posts: 9 Rating: (0) |
Hello. How can i change state of the of the softkey from the website? I tried add the softkey block to the variable memory configuration table but i can't |
6/30/2020 3:02 PM | |
Joined: 12/18/2014 Last visit: 5/15/2024 Posts: 33042 Rating: (4082)
|
So I would solve that for the extended web server. |
6/30/2020 3:26 PM | |
Joined: 12/18/2014 Last visit: 5/15/2024 Posts: 33042 Rating: (4082)
|
What do you mean with panel? LOGO! display? |
6/30/2020 3:32 PM | |
Posts: 9 Rating: (0) |
Yes Logo display or TDE. |
Last edited by: rafalk_26 at: 06/30/2020 15:33:05 |
|
6/30/2020 5:02 PM | |
Posts: 9 Rating: (0) |
OK. On The message text i put the status of pulse relay like example auto or manual Mode and next to it we place the softkey to change this Mode. |
6/30/2020 11:11 PM | |
Posts: 9 Rating: (0) |
I did the function as agreed. Logo display: Logo webserwer: |
7/1/2020 4:16 AM | |
Joined: 12/18/2014 Last visit: 5/15/2024 Posts: 33042 Rating: (4082)
|
It shows good.... |
7/1/2020 9:27 AM | |
Posts: 9 Rating: (0) |
Yes. Thanks for your help |
This contribution was helpful to1 thankful Users |
5/13/2021 12:25 PM | |
Posts: 41 Rating: (1) |
Now, when the software switch B002 is set to "on", the mode switches to "Auto" as expected. |
Last edited by: rwbrt at: 05/13/2021 12:25:24 |
|
Follow us on