9/11/2013 5:03 PM | |
Joined: 12/7/2011 Last visit: 5/17/2024 Posts: 384 Rating: (9) |
Hi to all, I have a problem withComunication between WinCC 7.2 and S7-1500 cpu. In WinCC project i have configured the "SIMATIC S7-1200 S7-1500 Channel" as in the attached file. CPU side, i have only configured the IP addres, set the "full access (no protection)" in the cpu property, and unset the "Optimized block access" in the DB property that i want to read. When i start the runtime, the comunication stay disconnected and i dont knows why. The strange thing is: In the comunication manual, i read:"Select in the context menu of the channel unit "TCP / IP" the Newconnection. "This will open the dialogConnection Properties ". But, as you can see in the attached file, there is no one"TCP / IP" channel but only "OMS+" Could anyone help me. Thanks Alfredo. AttachmentBinder1.pdf (1656 Downloads) |
Last edited by: Alfredo@as99 at: 9/11/2013 5:08 PM |
|
9/13/2013 2:42 PM | |
Joined: 12/7/2011 Last visit: 5/17/2024 Posts: 384 Rating: (9) |
I billwest, As you can see in the attached file, i have checked the acces point in the PG-PC interface, but the problem still present. I dont know what i wrong, but in can not fix the problem. One question: I have to also install the SIMATIC NET for a right functionality? Thanks Alfredo
AttachmentAcces point.pdf (1588 Downloads) |
Last edited by: Alfredo@as99 at: 9/13/2013 2:43 PM |
|
9/13/2013 3:10 PM | |
Posts: 510 Rating: (117) |
Yes! you must install SIMATIC Net. billwest |
9/13/2013 5:36 PM | |
Posts: 510 Rating: (117) |
Here is a link for SIMATIC Net Compatibility: http://support.automation.siemens.com/WW/view/en/9859007 SIMATIC Net V7.1 is compatible with WinCC V7.2 and Windows XP SP3 SIMATIC Net V8.2 SP1 is compatible with WinCC V7.2 and Windows 7 64 bit with or without SP1, Windows 7 32 bit with or without SP1, Windows Server 2008 R2 SP1Standard or Enterprise 64 bit These are the choices avaialble to you. billwest |
This contribution was helpful to2 thankful Users |
1/15/2014 7:22 PM | |
Posts: 5 Rating: (0) |
i have the same problem but with s7 1200. I have wincc 7.2 , i have connected the plc and the pc via the ethernet port but wincc can't communicate with plc. i have attached pictures. what i do wrong?
Attachmentwincc7.2.pdf (1393 Downloads) |
1/16/2014 8:55 AM | |
Posts: 5 Rating: (0) |
1. No i haven't change the name of access point.As i know, s7 protocol suite isn't suitable for s7 1200, for this reason i have chosen simatic s7-1200, s7-1500 channel. I tried with s7 protocol suite but it didn't work again. i saw in link below http://www.youtube.com/watch?v=92ylAUJ6ghQ and i did the same but nothing. i attached a photo with my all access point. 2. yes, Broadcom is a wireless interface. PlC is connected in a router. But i have tried to connect plc and my laptop with ethernet cable (Intel Gigabit interface in set pc/pg interface) but it didn't work.
Attachmentaccess point.pdf (888 Downloads) |
1/16/2014 4:20 PM | |
Posts: 510 Rating: (117) |
Loukas, When the Access Point in the connection shown in the Configuration Studio is associated with a valid network connection in the the PG/PC Interface and you can PING the PLC from the WinCC computer, you should be connected. See the attachment. Goog Luck, billwest
AttachmentWinCC_1500_Connection.pdf (1591 Downloads) |
9/18/2014 5:27 AM | |
Joined: 10/29/2007 Last visit: 5/15/2024 Posts: 59 Rating: (1) |
HiAlfredo@as99 I have same problem like you. There is no one"TCP / IP" protocolbut only"OMS+" inThe "SIMATIC S7-1200, S7-1500 Channel" channel. Did you slove your problem? Could you tell me how to slove this problem? An other question is: Can i use IE General port instead CP 1612,CP1613, CP1512as recomments from siemens? CP1612 was discontinuation, so can I use CP1612A2 instead CP1612?
|
6/21/2017 12:44 AM | |
Posts: 510 Rating: (117) |
I have attached a Step by Step for getting your S7-1500 connected to your WinCC V7.4, I hope this helps you. Good Luck! billwest AttachmentWinCC74_1500.pdf (739 Downloads) |
This contribution was helpful to2 thankful Users |
6/22/2017 10:09 PM | |
Posts: 10 Rating: (0) |
HI EVERYONE! Finally i solved it! I found the solution on this link: https://support.industry.siemens.com/tf/WW/en/posts/connection-between-pc-station-and-plc-s7-1500/122927?page=0&pageSize=10 On the PDF that i re-attach here and with the instructions of billwest. Really thx, if you need some help carefully read the attached pdf. A OPC was needed in order to communicate with 1500 and Panel PC. Attachment39960679_S7-1200_OPC_SIMATIC-NET_TIA-Portal_e.pdf (559 Downloads) |