1/28/2008 9:19 AM | |
Posts: 19 Rating: (0) |
how can i delete? and I want to IO directly. So how will I know the IO address? Is there any useful way? |
1/28/2008 9:39 AM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hi, yous see value "0" or "???" ? Regards Christoph |
1/28/2008 9:49 AM | |
Posts: 19 Rating: (0) |
I askedhowto delete the I/O variables on the first PZD. I tried the other way but Could not observe the outputs. |
1/28/2008 9:50 AM | |
Posts: 19 Rating: (0) |
I see nothing. |
1/28/2008 11:37 AM | |
Posts: 19 Rating: (0) |
I have attached jpg file. |
1/28/2008 5:22 PM | |
Posts: 19 Rating: (0) |
I HAVE ATTACHED THE SCREENSHOT. |
1/29/2008 10:02 AM | |
Posts: 19 Rating: (0) |
the reason of the error is IO configuration. When I delete PQW 346 from IO variables, then no alarm occurs. Is there any problem with Firmware v4.1 ? |
1/29/2008 12:09 PM | |
Posts: 19 Rating: (0) |
I USE NOW FREE TELEGRAM BUT STILL CANT OBSERVE THE OUTPUTS. WHEN I TRY TO CPU TO YHE RUN MODE IT GOES TO STOPU. I COULD NOT SOLVE THIS PROBLEM |
1/29/2008 12:38 PM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello, please look at the Diagnosticbuffer on the CPU why she goes to StopU. Regards Christoph |
1/29/2008 12:43 PM | |
Posts: 19 Rating: (0) |
Operating mode STOP_U reached Operating mode transition:Transition aborted by module: 4449h Error in I/O configuration So howmustIconfigureIOs? |
1/29/2008 3:19 PM | |
Posts: 19 Rating: (0) |
I HAVE SOLVED THE PROBLEM. I THINK I HAVEMADEYOUTIRE THANK YOU FOR ALL. |
4/17/2008 10:59 AM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello, which versions you use? Can you send the diagnosticbuffer if the error occurs? Regards Christoph |