6/22/2018 1:15 AM | |
Joined: 10/20/2015 Last visit: 5/12/2024 Posts: 94 Rating: (19) |
Hello GUY7ON, A possible solution. AttachmentTimer.zip (280 Downloads) |
6/25/2018 9:58 AM | |
Posts: 51 Rating: (0) |
Hi This is what i have already done, however when it get to 1 minute the minute column flashes up with a 1 then goes back to the hashtag |
6/25/2018 9:59 AM | |
Joined: 12/18/2014 Last visit: 5/21/2024 Posts: 33068 Rating: (4084)
|
Here's an example of how you can split the time measured by the stopwatch in hours and minutes. The hours are stored in VW0, the minutes in VW2. AttachmentSplitting.zip (202 Downloads) |
6/25/2018 10:07 AM | |
Joined: 12/18/2014 Last visit: 5/21/2024 Posts: 33068 Rating: (4084)
|
And here the same for splitting in minutes and seconds on time base "seconds".
AttachmentSplitting_minutes_seconds.zip (187 Downloads) |
6/25/2018 10:35 AM | |
Posts: 51 Rating: (0) |
i don't need to calculate any more than 8 hours, so is this possible? |
6/25/2018 10:48 AM | |
Posts: 51 Rating: (0) |
ok so how can i make this calculation? do i need to use a mathematical instruction? |
6/25/2018 11:01 AM | |
Joined: 12/18/2014 Last visit: 5/21/2024 Posts: 33068 Rating: (4084)
|
I make you an example. |
6/25/2018 11:02 AM | |
Posts: 51 Rating: (0) |
thank you |
6/25/2018 11:21 AM | |
Joined: 12/18/2014 Last visit: 5/21/2024 Posts: 33068 Rating: (4084)
|
Here's the example.
AttachmentCalcute_percent.zip (153 Downloads) |
6/25/2018 2:17 PM | |
Joined: 12/18/2014 Last visit: 5/21/2024 Posts: 33068 Rating: (4084)
|
The problem arises from the fact that the LOGO! dominated only fix point values. So I had to extend the program a bit. I did not notice that because I set the time base to test for seconds instead of minutes. I have now suppressed the mistake. AttachmentSplitting_in_hours_and_minutes_V2.zip (172 Downloads) |
6/25/2018 2:42 PM | |
Joined: 12/18/2014 Last visit: 5/21/2024 Posts: 33068 Rating: (4084)
|
Yes, that's correct. B005 is now for the hours (VW0) and B003 for the minutes (VW2). This had to be corrected in the parameter VM mapping. Is corrected in the attached program. AttachmentSplitting_in_hours_and_minutes_V3.zip (157 Downloads) |
6/25/2018 2:46 PM | |
Posts: 51 Rating: (0) |
Superb thanks so much for your support with this, its on test now :D |
This contribution was helpful to1 thankful Users |
6/25/2018 3:02 PM | |
Joined: 12/18/2014 Last visit: 5/21/2024 Posts: 33068 Rating: (4084)
|
Is your problem solved now? |
6/25/2018 3:37 PM | |
Posts: 51 Rating: (0) |
This now works perfectly! the only thing i need to do now is to integrate the percentage calculator to measure the difference in a separate box :) |
6/25/2018 3:41 PM | |
Joined: 12/18/2014 Last visit: 5/21/2024 Posts: 33068 Rating: (4084)
|
That sounds good. Do you get that alone? |
6/25/2018 3:46 PM | |
Posts: 51 Rating: (0) |
I will have a go first :) thanks for the help |
This contribution was helpful to1 thankful Users |
6/26/2018 9:47 AM | |
Posts: 51 Rating: (0) |
Don't worry I got it working! :) thanks again :) |
This contribution was helpful to1 thankful Users |
Follow us on