Here's the example.
AttachmentCalcute_percent.zip (154 Downloads) |
6/25/2018 2:17 PM | |
Joined: 12/18/2014 Last visit: 6/1/2024 Posts: 33137 Rating: (4094)
|
The problem arises from the fact that the LOGO! dominated only fix point values. So I had to extend the program a bit. I did not notice that because I set the time base to test for seconds instead of minutes. I have now suppressed the mistake. AttachmentSplitting_in_hours_and_minutes_V2.zip (173 Downloads) |
6/25/2018 2:42 PM | |
Joined: 12/18/2014 Last visit: 6/1/2024 Posts: 33137 Rating: (4094)
|
Yes, that's correct. B005 is now for the hours (VW0) and B003 for the minutes (VW2). This had to be corrected in the parameter VM mapping. Is corrected in the attached program. AttachmentSplitting_in_hours_and_minutes_V3.zip (158 Downloads) |
6/25/2018 2:46 PM | |
Posts: 51 Rating: (0) |
Superb thanks so much for your support with this, its on test now :D |
This contribution was helpful to1 thankful Users |
6/25/2018 3:02 PM | |
Joined: 12/18/2014 Last visit: 6/1/2024 Posts: 33137 Rating: (4094)
|
Is your problem solved now? |
6/25/2018 3:37 PM | |
Posts: 51 Rating: (0) |
This now works perfectly! the only thing i need to do now is to integrate the percentage calculator to measure the difference in a separate box :) |