6/3/2020 10:17 AM | |
Joined: 8/19/2019 Last visit: 11/14/2023 Posts: 20 Rating: (0) |
Yes, you understood well! |
6/3/2020 10:19 AM | |
Joined: 12/18/2014 Last visit: 6/5/2024 Posts: 33151 Rating: (4095)
|
Then you have to better explain where your problem is .... |
6/3/2020 10:33 AM | |
Joined: 12/18/2014 Last visit: 6/5/2024 Posts: 33151 Rating: (4095)
|
Why set you the gain in the PI Controller to 10? That make no sense... Let it be by 1. |
6/3/2020 10:49 AM | |
Joined: 8/19/2019 Last visit: 11/14/2023 Posts: 20 Rating: (0) |
i don't know how to program the part to keep the pressure at 3bar |
6/3/2020 11:26 AM | |
Joined: 12/18/2014 Last visit: 6/5/2024 Posts: 33151 Rating: (4095)
|
If I understand you correctly, you want to prevent the pressure from dropping below 3 bar. I have created a program proposal for you. To get a better control range, I set the analog amplifier for a higher resolution (with two decimal places). The setpoint for the controller can be entered on the display. The controller is set for upward regulation. This means that if the actual value is greater than the setpoint, the analog output outputs 0 volts. The further the pressure drops below 3 bar, the more the voltage of the analog output rises to a maximum of 10Volt. AttachmentPI control_V2.zip (114 Downloads) |
6/3/2020 12:04 PM | |
Joined: 8/19/2019 Last visit: 11/14/2023 Posts: 20 Rating: (0) |
Thank you very much! |
6/3/2020 1:06 PM | |
Joined: 12/18/2014 Last visit: 6/5/2024 Posts: 33151 Rating: (4095)
|
Hello Savin.ct you're welcome ... |