2/12/2020 10:17 AM | |
Joined: 4/28/2015 Last visit: 9/20/2024 Posts: 397 Rating: (56)
|
Hello, if you raise the motion control ressources, you will get a compiling error in TIA Portal... With SIMATIC S7-1516 you get 2400 motion control ressources. If 90% are in use, there are only 240 motion control ressources left. And for each positioning axis you will need 80 ressources, that means 400 motion control ressources more... And this is too much for this SIMATIC S7-1516 CPU... Possibilities to solve the problem:
|
This contribution was helpful to1 thankful Users |