9/19/2008 3:29 PM | |
Joined: 12/20/2005 Last visit: 7/12/2023 Posts: 79 Rating: (4)
|
Sreeram, Assuming you want to pass data from QUADLOG to the S7 controller, you could put an Industrial Ethernet Module (IEM) in between the two to act as a gateway from Industrial Ethernet (on the S7 side) to Modulbus (on the QUADLOG side): http://support.automation.siemens.com/WW/view/en/26093185 Note - the current IEM release does not support safety-rated or fail-safe communications between QUADLOG and S7, however I am told that this is coming soon. Another option would be MODBUS serial communications. Regards, RJP |
9/20/2008 8:31 AM | |
Posts: 53 Rating: (0) |
Dear RJP Thanks for your valuable feedback. Will check it up and get back to you shortly. Regards Sree |