1/18/2021 12:31 PM | |
Joined: 10/11/2006 Last visit: 9/27/2024 Posts: 5908 Rating: (804) |
Hello, you get 4096 steps/revolution. 157 mm / 4096 Inc. = 0,038330078125 mm/Inc. With Motioncycle of x ms you get minimal velocity of x mm/s 1ms => 0,038330078125 mm/Inc. * 1000 = 38 mm/s 2ms => 0,038330078125 mm/Inc. * 500 = 19mm/s 4ms => 0,038330078125 mm/Inc. * 250 = 10 mm/s 8ms => 0,038330078125 mm/Inc. *125 = 5 mm/s Use the full resolution of 4096 and increase the motioncycle if necessary. 2.3 Technology module TM PosInput 2 https://support.industry.siemens.com/cs/ww/en/view/109486133 |
With best regards, |
|
This contribution was helpful to2 thankful Users |
1/19/2021 1:25 PM | |
Joined: 3/23/2015 Last visit: 4/18/2024 Posts: 16 Rating: (0) |
Thanks, this solved. I imagine I've to use Actual value extrapolation and then read filteredvelocity instead of actual velocity to smooth out the readings. |
Follow us on