2/26/2014 4:26 PM | |
Posts: 10 Rating: (0) |
.
AttachmentSKIP.zip (345 Downloads) |
3/1/2014 5:57 PM | |
Posts: 10 Rating: (0) |
Hi I check the set value in r447 that is 80%,24%&10% respectively as we set.(drive first operate at 40 HZ then we reduce the speed from 40 to 12 & at last at 5 HZ through limit switches) we also check the all DI signals n all are O.K...the main problem is one drive trip in F053 fault(when drive trip on f053 drive current increses than normal running) n after that another trip in F015 bcz total load transfer on one motor.normally both motor current is almost equal but a the time of tripping on F053 that drive current increases .we also check Encoder n cable both are o.k..n this happen only when load on skip car is more..I am attaching here drings of skip car..
AttachmentSkip Dwg.zip (352 Downloads) |
3/3/2014 4:22 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (876) |
Please check P492 & P498, values are 180% & -180%bothdrives. |
3/3/2014 12:44 PM | |
Posts: 10 Rating: (0) |
Both drive P492 & 498 are..110 & -110%..at present. |
3/5/2014 8:20 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (876) |
Does your problem solved? |