Hello Nuno_ Basic Panels (1st + 2nd Generation) cannot perform scripts, so you cannot use this templates. I think the only way to implement an own screensaver would be to use the PLC with a workaround. Use a timer in the PLC and by operating on the panel reset on every operator button the timer again in PLC. If the timer is executed use a Screenchange from the PLC in the HMI to your screensaver screen. https://support.industry.siemens.com/cs/ww/en/view/93909293 Here use a transparent Button ober the whole screensaver screen and use a screenchange to your rootscreen and reset again your timer in the PLC (it would only be a workaround but the Basic Panels do not have very much functionality...) Bye Murof |